[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: rochester cooling problems
Merle,
First, thanks for offering help.
The design runs the two cooling heads in series, just to prevent the
problem you suggest. This results in the downstream cooling head getting
warmer water than the upstream one. One solves this problem by just
running a high enough flow rate so that the temperature rise is not
significant. In this case, with a cooling load estimated to be 25 W per
head, this requires about 10 gallons per hour to keep the difference in
cooling temperature to the two heads to a few degrees F.
The TEC sits on a cooling plate where there is a meander milled into the
back side. The thickness of the plate is 1/16" in the meander to limit the
temperature drop through the plate. The large area of the meander insures
good thermal contact between the cooling fluid and the aluminum cooling
plate. There is an aluminum block on top of the TEC which contains the
thermometer, then a grease joint to the back of the CCD. The TEC is glued
to the aluminum plate with silver filled epoxy, there is also a glue joint
between the aluminum block containing the thermometer and the TEC. In the
early days, these glue joints sometimes failed. This would result in poor
thermal contact. Now I use better glue technique. Now they really stick
and I have to destroy the TEC to get it off to replace it.
The design is such that forces on the TEC do not change significantly with
temperature changes, etc. It is free to move in the stack direction, being
constrained only by the pressure supplied by the deformation of a thin
printed circuit board with provides a few ounces per square inch
compression. There is nothing leaning against the stack to provide a shear
force.
There are a number of systems working of identical design where the
expected cooling is achieved. This points to a failure of the TEC and not
a design problem. While there are a number of places where a failure could
occur, experience points to a failed TEC. These units are very
fragile. They can stand some compression, but fail easily in tension or
shear. The mount is designed to provide a proper mount. It is mounted in
mild compression. I have seen the units fail from shock, and tension as
when the thermal grease joint is pulled apart.
As I have pointed out in previous e-mails, the TECs are easy to break in
tension. Just a few pounds of force required to pull the CCD off the
aluminum block will do it. I have learned to gently work the grease joint
back and forth to gradually break it free. The also break from
shock. Just dropping a camera head a few inches on to a concreate floor
has done it. I measure the health of a TEC by measuring the current at a
set voltage. Good ones draw a high and constant current. Bad one carry
much less current which generally decreases over time.
I just looked at the data sheets, and the solder used to assemble the
junctions melts at 135 C. One might try to heal the TEC by heating it up
to 130 C or so. But this would probably damage the electrolytic
capacitors. Most of the other parts would stand it. So not much can be
done other than to take the unit apart and replace the TEC. Looking at the
data sheet, they claim the device will stand hundreds of pound of force in
tension and shear. Don't believe it. No doubt such tests were made by
some uniform force machine. In practice you bump them and the force is far
from equal. So the weak overstressed device fails. Sigh! I note that the
data sheet recommends mounting in compression of several hundred
psi. Possibly they might fail less easily if mounted in higher
compression. It is really too late to design a different loading scheme
now, since the design is complete, and most units continue operating once
installed.
Tom Droege
At 04:08 PM 1/10/02 -0800, you wrote:
>Michael,
>I have been reading the TASS e-mail for two years. I think I can help
>here. I detect either a hydraulics problem or a heat transfer problem.
>
>I take it you are cooling two CDs with one pump. Apply the conservation
>of mass. With one source of flow and pressure you must evenly split
>(divide) the flow between the two coolers. That means the same diameters,
>lengths, and fittings on the two parallel lines. The pump output is also
>divided evenly. If you have a design that requires a certain flow rate,
>the "rule of thumb" is to choose a pump design where the design point is
>75% of the pump rating.
>
>The heat transfer problem may be inadequate contact between the CD and the
>cooler.
>
>I would recommend that you tackle one problem at a time, eliminating each
>one until the real culprit is found.
>
>Merle Jephson-King